One 7kW charger will need 30A; two would need 60A. If your property has a 100A supply that would still leave 40A (around 10kW) available for other uses. Very few houses actually use 10kW at any instant and if you were wanting to do your charging between (say) MN & 6am you might even be able to run 3 chargers (90A) at once with the remaining 10A being enough for a small background load.
Your commitment to an aggressive diversity calculation does you credit, but your home won’t meet any kind of wiring regulations if you specify it like that.
If you look at the fuses in your consumer unit they look massive. And yet they still trip and even blow completely on occasion.
Every circuit in your home has a specification set out in the current version of the wiring regulations and the EVSE installers have to comply with the latest version on any work they do irrespective of when the property was constructed.
So if you have a gas boiler and a gas cooker your 32A cooker circuit probably looks like massive overkill but if you have an electric hob and an electric oven when you cook Christmas dinner with it all switched on, you may actually exceed the rating in the circuit while you heat the oven(s) up.
And let’s hope you don‘t live anywhere with an electric shower. Or night storage heaters!
There is some allowance for the fact that everything isn’t switched on at once (diversity in demand calculation) but the required specifications are still massively over what you’d think you actually use. That’s why you have a 60A fuse in the first place. Because you might turn everything on at once.
There is zero diversity allowed on an EVSE and any installer will look at your 60A circuit and just say no. No install possible. Even on an 80A circuit they might limit you to 16A or 30A rather than the full 32A. Andersen will not allow one of their authorised installers to install an Andersen EVSE on a circuit fused at less than 100A.
So while you may be correct, you won’t get a qualified installer to do what you suggest. You can’t have two 7.4kW EVSEs charging on a 100A fused single phase supply. You get two sharing 7.4kW which typically means 3.6kW each.
If you install them yourself your theoretical calculations may be correct, and I hope they are because the energy required to melt a 100A fuse will be pretty spectacular to behold.
If you want to charge two cars at 7.4kW you pretty much need a 3-phase supply. At which point you can charge two cars at 11kW. Which is rather lovely.